    I'm not sure what there is in there.  Heard vague recollection of a
    pair of CAT5s in there, but not with any certainty.  This is why we
    need to go survey the place.  I would expect their grounds to be
    tied given the power system changes, and the conduit to be bonded. 
    Worst case though we can omit the shield as CAT5 Ethernet is only
    magnetically coupled (has isolation transformers) and uses
    differential signaling.<br>
    <br>
    I'm kind of hesitant to introduce fiber to HamWAN where it's not
    absolutely necessary.  We have enough problems with proper RJ45
    terminations, never mind asking people to re-terminate fiber if
    something breaks.<br>
    <br>
    --Bart<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 6/1/2020 10:01 AM, Tom Hayward
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAFXO5Z3U81QfuCbiR6Yn+iBa9NYoGC+3pNj7w0yxRJRcahf8wg@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div dir="ltr">On Sun, May 31, 2020 at 11:35 PM Bart Kus <<a
            href="mailto:me@bartk.us" moz-do-not-send="true">me@bartk.us</a>>
          wrote:<br>
        </div>
        <div class="gmail_quote">
          <blockquote class="gmail_quote" style="margin:0px 0px 0px
            0.8ex;border-left:1px solid
            rgb(204,204,204);padding-left:1ex">
            <div>Kenny, a great question that I forgot to make clear. 
              There is already conduit between all the buildings.  I
              confirmed tonight that it's got sufficient capacity to run
              an extra CAT5.  I think we only have to fish a ~150ft run
              between the middle building and the bunker, as there are
              spare CAT5s in the conduit between the middle building and
              north building, so that should just be plug-n-play.  The
              trenching to the bunker was done earlier this year as a
              response to the awful power outages we suffered this
              winter.  The north building is now tied into generator
              control (and possibly power?) of the bunker.<br>
            </div>
          </blockquote>
          <div><br>
          </div>
          <div>Does the conduit already carry a conductor? I would avoid
            installing anything but fiber between buildings to simplify
            grounding/isolation.</div>
          <div><br>
          </div>
          <div>Tom</div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
PSDR mailing list
<a class="moz-txt-link-abbreviated" href="mailto:PSDR@hamwan.org">PSDR@hamwan.org</a>
<a class="moz-txt-link-freetext" href="http://mail.hamwan.net/mailman/listinfo/psdr">http://mail.hamwan.net/mailman/listinfo/psdr</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>